Hello everybody,
I have a pump driven by a Heemaf motor 380VAC, 196 A current load, I wonder how big the cable i want to use to supply this motor from 450 meters far power supply.
Thank you
Hello everybody,
Thank you
I think DOL contactor will hold for voltage drop of up to 35℅. So such oversizing cable may not be necessary.Now, the problem will be at start. If your motor is provided with VFD drive then this cable is good. If you have to start it D.O.L.[direct-on-line] then the pf=0.25 but the current will be 7*196 A so you need 4 parallel cables of 3*240 mm^2 copper[15% voltage drop].
Thank you, Sahib. From our experience-power stations-the starting voltage has to be so high in order to produce at least 50% of the rated torque.
With respect to IEC 60034-12 Rotating_electrical machines Part 12: Starting performance of single-speed three-phase cage induction motors
Table 1 - Minimum values of torques for design N. the minimum voltage has to be:
For motor power equal or less than 16 kW 35%
For motor power equal or less than 160 kW 20%
That is recalculated on basis Tq=(Vstart/Vrated)^2*Ti [Ti= locked rotor torque-minimum]
However, it is not compulsory and it has to be verified for the specific case.![]()
You are right, topgone. I am very sorry. I forgot to reduce the starting current since the voltage decreasesA 3 X 240mm2 will do. The OP can be assured all other requirements are complied with.![]()