Randall-EE98
New User
- New Mexico
- DC Analyst
I am attempting to identify why DCIM, UPS, RPP loads are producing varying values in calculations and metering. The loads are both 120V and 208V single phase from electronic devices (computers and network electronics) connected to 120V, 208V single phase and 208V 3-phase power strips. The 208V single & 3-phase power strips have C13 & C19 receptacles, so the electrical device loads are 208V single phase loads however fed from an upstream 2-pole or 3-pole branch circuit breakers. The RPP's have 4 225A, 42 slot panels each. The RPP display provides the Amps for A, B, C & neutral for each panel. The branch circuit metering is not accurate (incorrectly wired CT's, incorrect schedules etc. so DCIM calcs are not correct). That is what I am trying to remediate. The metering data that should be relatively accurate is the RPP A, B, C, N values and the UPS(s) total power and phase Amps. Power factor is close to 1 (computers are efficient heaters).
Here are the values from 2 panels: #1 L1-22A, L2-32A, L3-32A, N-10A #2 L1-37A, L2-39A, L3-25A, N-3A
Is there enough info without branch circuit Amps to calculate the total power consumption per panel? Thanks for any help.