I am reviewing a project and noticed ANSI Power CB (2000A) is feeding a UL 891 MLO switchboard(2000A) downstream. There is a short time delay of 12 cycles on the Power CB for the coordination with the MCCBs in the switchboard.
Since UL 891 switchboard is only rated for 3-cycle, I don't think The upstream ANSI PCB (12-cycles) can protect the the downstream switchboard, if there is a fault at the bus in the switchboard. Is that right? I think the solution is they should have a MCB at the switchboard for the bus fault and the upstream PCB will protect the feeder fault only. Any thoughts?
Since UL 891 switchboard is only rated for 3-cycle, I don't think The upstream ANSI PCB (12-cycles) can protect the the downstream switchboard, if there is a fault at the bus in the switchboard. Is that right? I think the solution is they should have a MCB at the switchboard for the bus fault and the upstream PCB will protect the feeder fault only. Any thoughts?