Re: Power Circuit Breaker Trip Unit Replacement
Some things to consider:
1. Control Power - the trip unit is powered by the breaker CT's; external power is not required to trip the breaker. (It may be required to read a display.) The new external relay will require a source of control power, usually a DC battery system. AC control power could be affected during a fault. A capacitor trip device might solve the problem. Power is needed to operate the relay and to trip the breaker.
2. Tripping Means- the trip unit uses a flux transfer trip release device that requires very little power. It can only be wired to the breaker mounted protection module. You will need to add a trip solenoid to the breaker if it is not already equippped with an electrically actuated remote trip. This may require adding extra secondary disconnects to the breaker.
3. Current Transformers - the DSL breaker?s CT's for the trip unit cannot be wired to a normal relay. They are not 5 amp rated CT?s. You will need to add CT's to the breaker stabs and run them to the relay. Verify that there is enough room in the breaker cubicle to do this. Make sure to get polarities and grounding correct.
4. Ground Fault Protection - if the system is 3-phase, 4-wire and ground fault protection is needed , you will need to add a another neutral CT and make sure it gets wired in with the correct polarity on the correct circuit. (Sounds easy, but I have seen many done incorrectly.)
If the owner needs to do the conversion anyway to get the correct coordination with other breakers, look at just adding the new relay and not removing the trip unit. Set the trip unit's curves above the new relay curve as a backup. That way, you will still have protection if the control power fails or the trip circuit blows a fuse, and you haven't applied the breaker in a manner that might violate the breakers listing. Any special protection features of the manufacturer?s design (like a high set instantaneous) would still be in service.
BTW, when we have looked at changing the trip units to get better coordination we noticed that the extent of the power outage was the same with or without proper coordination. (Same load was dumped whether the upstream or downstream breaker tripped.) The advantage of better fault location was not considered worth the cost and risk of device change out.
Good Luck,
Bob W.