I have a customer that currently has a 480V LV Switchgear lineup which feeds several MCC's. The SWGR lineup is M-T-M fed from two transformers.
They are looking to replace the LV SWGR as well as one of the MCC's closest to the switchgear and have a desire to have the SWGR and MCC combined into a single structure. It has been suggested to provide an MCC structure with Power circuit breakers for the M-T-M as well as the other feeders that feed downstream MCC's.
Are there any disadvantages to providing power circuit breakers in an MCC structure as opposed to a UL listed LV SWGR structure? A couple of things that come to my mind:
- Breakers may not have draw out capability in an MCC lineup.
-MCC lineup will have 3-cycle rating (as opposed to 30cycle for SWGR) which may not allow adequate coordination with mains
-Arc Flash - Since MCC structure will be considered as a single structure with no barriers the entire MCC would take on elevated AF rating (cant take advantage of AF reduction on Main breaker in separate structure like switchgear)
They are looking to replace the LV SWGR as well as one of the MCC's closest to the switchgear and have a desire to have the SWGR and MCC combined into a single structure. It has been suggested to provide an MCC structure with Power circuit breakers for the M-T-M as well as the other feeders that feed downstream MCC's.
Are there any disadvantages to providing power circuit breakers in an MCC structure as opposed to a UL listed LV SWGR structure? A couple of things that come to my mind:
- Breakers may not have draw out capability in an MCC lineup.
-MCC lineup will have 3-cycle rating (as opposed to 30cycle for SWGR) which may not allow adequate coordination with mains
-Arc Flash - Since MCC structure will be considered as a single structure with no barriers the entire MCC would take on elevated AF rating (cant take advantage of AF reduction on Main breaker in separate structure like switchgear)