mkgrady
Senior Member
- Location
- Massachusetts
Went to a customers home today and found symptoms of a loose neutral. This is my first experience with this type of problem. I found what I think leads to an indication of the incoming line having a bad neutral. The voltage on the service legs would go up and down as different loads would come on and off. The clue (I hope) that tells me the problem is out on the street is that the GEC had substantillly more current on it than the service neutral. The following is a set of readings at the main service panel: A leg to N 145 volts, B leg to N 96 volts, A leg current 8.4 amps, B leg current 14.7 amps, neutral current 2/10ths amps and finally GEC current 4 amps. I'm thinking the neutral is loose out on the street because of the high current on the GEC. Am I on to something? The customer is going to call the power company to check their neutral before I look any further.