I know using flexible cords as a substitute for a permanent wiring method is a NEC violation as well as having attaching it to a building.
In an industrial facility last week, I saw numerous truss mounted cooling fans that were using a bunch of IEC type power cord sets zip tied to bridal rings every 8ft or so. The thing I did not like was plugging multiple lengths of these cord sets together in order to reach a receptacle outlet. (40 or 50 feet)
The NEC covers "flexible cords" (Art 400) but types are defined per UL 62 and "power cord sets" per UL 817. This seems to render the above installation as ok because its a UL cord? I cant seem to find anywhere in the UL that prohibits plugging in multiple cord sets together provided the ampacity is not exceeded. Does this sound right to you?
In an industrial facility last week, I saw numerous truss mounted cooling fans that were using a bunch of IEC type power cord sets zip tied to bridal rings every 8ft or so. The thing I did not like was plugging multiple lengths of these cord sets together in order to reach a receptacle outlet. (40 or 50 feet)
The NEC covers "flexible cords" (Art 400) but types are defined per UL 62 and "power cord sets" per UL 817. This seems to render the above installation as ok because its a UL cord? I cant seem to find anywhere in the UL that prohibits plugging in multiple cord sets together provided the ampacity is not exceeded. Does this sound right to you?