We have 2-15HP and 2-7.5HP pump motors coming off the same MCC. Having issues with the 2 new 7.5HP motors failing on overtemp. Manufacture is saying we need Power Factor Correction Capacitor Bank installed to correct problem. I have my own beliefs as to why the overtemp BUT for arguement sake lets just say we do as manufacture suggests. OK so we do and here is what we see. Motor pulls about 6A per phase @ 480VAC before adding 3KVAR bank. We add bank to secondary side of breaker feeding starter (per manufactures installation instructions because of periodic bumping of motor which we do sometimes) and now we see about 3A per phase at breaker, about 3A per phase going to bank, and about 5.8A per phase going out to motor. So results are that we have dropped Amperage going to motor by about .2A but the interesting thing is at the breaker feeding the section where we have reduced by about 50%. Lets say we now have no motor fails on overtemp once again for argument sake. (time will tell) Ok so here are my questions.
#1. Do these readings seem right?
#2. Since the bank is wired in parallel to the secondary side of the breaker feeding the motor section which is always turned, do i really need a second bank for the second motor if only one will run at a time (since the bank is technically in parallel with the whole MCC at any given time)
#3. Only one 7.5HP will run at a time but there might be a time when both 15HP and 7.5HP are running. How will this affect the banks results? Thank you in advance....
#1. Do these readings seem right?
#2. Since the bank is wired in parallel to the secondary side of the breaker feeding the motor section which is always turned, do i really need a second bank for the second motor if only one will run at a time (since the bank is technically in parallel with the whole MCC at any given time)
#3. Only one 7.5HP will run at a time but there might be a time when both 15HP and 7.5HP are running. How will this affect the banks results? Thank you in advance....