Fulthrotl
~Autocorrect is My Worst Enema.~
- Occupation
- E
Industrial situation, gravel quarry.
4 conveyors, interlinked, staged starting,
biggest load first, to prevent largest inrush from being
stacked on top of running loads.
480V. 3Ph. Wye
Running Amps Starting Amps
A phase 217 364
B phase 219 364
C phase 217 361
Total KW 65
Total KVA 182
PF .355
THD .9%
largest motors (two 50 hp driving common shaft)
are on soft start, rest are across the line contactors.
service cycle is 40 hours continuous, once per month.
a number of starts and stops during that 40 hours,
but uninterrupted to the largest extent possible.
power factor right at 40% for all separate loads, as well.
i'm wondering if power factor correction might be warranted
here? my thought would be to correct it at the service with
a cap that would be switched off when the conveyors were
not in use, to prevent overcorrection.
is this even worth bothering about?
4 conveyors, interlinked, staged starting,
biggest load first, to prevent largest inrush from being
stacked on top of running loads.
480V. 3Ph. Wye
Running Amps Starting Amps
A phase 217 364
B phase 219 364
C phase 217 361
Total KW 65
Total KVA 182
PF .355
THD .9%
largest motors (two 50 hp driving common shaft)
are on soft start, rest are across the line contactors.
service cycle is 40 hours continuous, once per month.
a number of starts and stops during that 40 hours,
but uninterrupted to the largest extent possible.
power factor right at 40% for all separate loads, as well.
i'm wondering if power factor correction might be warranted
here? my thought would be to correct it at the service with
a cap that would be switched off when the conveyors were
not in use, to prevent overcorrection.
is this even worth bothering about?