goog morning every body, i hope you can help me.
a factory has a power factor of 75.21% and ask me to calculate the power factor for correcting above 90% and i did the following calculation:
the energy bill shows a peak demand load of 164 KW and a power factor of 75.21%.
i want to correct the power factor to 97%
KVAR = KW x (TAN(A)-TAN(B))
A = COS-1(0.7521) = 41.22
B = COS-1(0.97) = 14.06
KVAR = 164 x (TAN(41.22) - TAN(14.06))
KVAR = 164 x (0.87605-0.25044)
KVAR = 102.60
i propose to install a 100 KVAR capacitor but the maintenance engineer thinks that a 100 KVAR capacitor is too big, the factory has a 300 KVA, 13200-480/277 volts substation, it doesn't have equipment in 480 volts, has 4 dry transformers in main panelboard (150,75,75,45 KVA).
other person told to the enginner that a 30 KVAR capacitor was enough for improving the power factor, this factory makes toys.
the calculation that i did was correct or there is another method for calculating the correction of power factor.
KVAR = 102.60