Power Factor for voltage drop calculations for a commercial building .95?

Status
Not open for further replies.

Cartoon1

Senior Member
Location
Florida
Occupation
Electrical Engineer
Hello all,

Typically what do you use for PF when doing voltage drop calculations for a typical commercial building from its switchboard (480/277) to the subpanels? Nothing crazy, typical LED lights, Receptacles, Offices setup, step down transformers to 208/120V, and A/C. Is .95 reasonable or maybe even Pf of 1 since it is mostly resistive load?

Thank you
 
Hello all,

Typically what do you use for PF when doing voltage drop calculations for a typical commercial building from its switchboard (480/277) to the subpanels? Nothing crazy, typical LED lights, Receptacles, Offices setup, step down transformers to 208/120V, and A/C. Is .95 reasonable or maybe even Pf of 1 since it is mostly resistive load?

Thank you
Are you doing fault current calculations or simple VD?
 
Are you asking because (a) you have Watts and need to use an average PF to get VA to get the currents or (b) for AC voltage drop, even once the current is known, the power factor of the loading has an effect because of the reactance of the conductors?

For (b) the effect is small unless the conductors are physically quite large, as the reactance per foot is fairly constant with size, and only at very large sizes is the resistance per foot low enough that the impedance isn't simply dominated by the resistance.

If this is for a feeder with physically large conductors (MCM range, IIRC), then I would suggest looking at Chapter 9 Table 9 Note 2 and calculating the "effective Z" for PFs of 0.85 (easy, given in the table), 0.9, 0.95, and 1.0, and seeing if it makes much difference.

Cheers, Wayne
 