Power Factor Requirement

Status
Not open for further replies.

Leo Li

Member
Location
China
Occupation
Engineer
HI Friends,Is there any power grid or others requirement for new building 13.2KV-480V/277 sustation power factor in Massachusetts?Is this mandatory or optional?Thanks.
 

Leo Li

Member
Location
China
Occupation
Engineer
There are multiple power companies serving Mass. and they may have differing requirements. Typically, many utilities require a PF of 0.90 lagging or higher but that can also depend on the rate structures for a given location or customer.

For example, NationalGrid says "Customers are encouraged to maintain a power factor near 95 percent" (https://www.nationalgridus.com/media/pronet/constr_esb750.pdf)
Thanks Sir!
 