"IN AN EXISTING SERVICE CALC, RE-CONFIGURATION,
POWER FACTOR CONSIDERATION, ADDITION IS FOR ALL USED MOTORIZED EQUIPMENT "
??????

THANK YOU
 

kwired

Electron manager
Location
NE Nebraska
HI
"IN AN EXISTING SERVICE CALC, RE-CONFIGURATION,
POWER FACTOR CONSIDERATION, ADDITION IS FOR ALL USED MOTORIZED EQUIPMENT "
??????

THANK YOU
Yes and no.

NEC load calculations generally are done using VA. So the PF (high or low) is already accounted for in whatever VA you plug into your calculations.
 

Toros

Senior Member
Location
Tujunga, CA
Yes and no.

NEC load calculations generally are done using VA. So the PF (high or low) is already accounted for in whatever VA you plug into your calculations.




i think, i have to include pf because of used motorized equipment that were new in the beginning
???????
 

kwired

Electron manager
Location
NE Nebraska
i think, i have to include pf because of used motorized equipment that were new in the beginning
???????
When doing motor circuit calculations - you are supposed to use full load currents in tables 430 part XIV. For the AC motors those values are for the most inefficient and lowest power factor motors you would likely ever find - so power factor is already included in the FLA you will use for each motor. Most of the time you will be designed to carry much more current then you actually have on a feeder or service with many motors on it.
 