Power Factor

Status
Not open for further replies.

OldNewbie

Member
In a electric utility system with almost completely heavy industrial loads, what would be a "decent" power factor? Any power company engineers out there want to offer a comment?

Old
 
Tough to say since those types of facilities usually have capacitor banks to offset power factor issues.
 
OldNewbie said:
In a electric utility system with almost completely heavy industrial loads, what would be a "decent" power factor? Any power company engineers out there want to offer a comment?

Old
Decent- expected- would be around .8 without correction
That does not mean that you won't be severey penalized by the utility when it is less than .95 or higher
 
If you're referring othe utility's power factor it depends on where exctly along the line you are. When I worked for a utility, we placed capacitors using an economic analysis that present worthed the savings. We optimized dollars saved. Since the capacitor banks are lumped along a distribution line, say 1200 kvar or 1800 kvar, the pf changes significantly at each installation. That being said, I imagine a .9 or so overall pf is good in a distribution system.

Jim T
 
in the Philippines, utilities used to give a teensy amount of discount if your p.f. is 85 and above and will penalize you if you have a p.f. below 80
 
Last edited:
Hi, I have another question:

Lets say we have a power factor corrector installed at the mains, will adding capacitors or changing to HPF ballasts to our fluorescent lightings still matter?

Thanks.
 
We penalize below 85% and get penalized from our supplier if we lag below 95% or lead at all. I am in the southeast under the TVA umbrella and that is the way it works just about all over the valley. I would concur that .8 would be a good PF before correction.
 