I have a question regarding power feed to an equipment.
The equipment is a 450hp compressor and it demands 480 VAC. The distance between the compressor and Substation from where we have planned to feed it is 600ft.
We have done the cable sizing and found that 2 parallel runs of 3C X1 500 kcmil is good for the feed.
But at present there is a feed available from the Substation to a panel having distribution block in it, half way around 400ft having cable of 3 runs of 3C X1 of 500kcmil.
So my questions are:-
1) Can we reduce the cable size for remaining 200ft, considering there is less voltage drop for the first 400 ft as it has 3 runs and then make 2 runs of 350 kcmil?
2) Is it allowed to change the size of cable feeding same equipment half way.