I'm GC on my own renovation job and have been through 2 electricians and POCO on a problem with no resolution. Thought the great minds here might be able to give me some thoughts on where to point the next electrician or POCO.
Problem: All lights and appliances dim/loose some power when others are operated. Any power draw on any circuit causes fluctuation on all others. Lights pulsate to the washer motor, interior/exterior lights dim when the 1/4 hp sump pumps kick on. Toaster dims the range hood motor.
Back ground: Condition may have existed prior to purchase of property. Since purchase, 90% of the wiring is new, last 10% will be soon. New garage and kitchen additions all code, no shared circuits (recps and lighting separate). Biggest draws are 4 tn heating/cooling, 80gal water heater. Kitchen is gas. Few dozen recessed lights on dimmers.
All neutrals are tight at panel and branch circuits and appliances. All lighting circuits and receptacles work normally. (2) shared neutrals in old wiring but they were pulled and still no change in condition.
POCO replaced over head neutral due to tree rat damage and it appeared to resolve problem for a breif period. (Maybe it was just an illusion). Since return of problem, they have checked twice and declared power to both leg fine.
What isn't being looked at? What should be tested next? What are the code words that POCO responds to? Thanks.
Problem: All lights and appliances dim/loose some power when others are operated. Any power draw on any circuit causes fluctuation on all others. Lights pulsate to the washer motor, interior/exterior lights dim when the 1/4 hp sump pumps kick on. Toaster dims the range hood motor.
Back ground: Condition may have existed prior to purchase of property. Since purchase, 90% of the wiring is new, last 10% will be soon. New garage and kitchen additions all code, no shared circuits (recps and lighting separate). Biggest draws are 4 tn heating/cooling, 80gal water heater. Kitchen is gas. Few dozen recessed lights on dimmers.
All neutrals are tight at panel and branch circuits and appliances. All lighting circuits and receptacles work normally. (2) shared neutrals in old wiring but they were pulled and still no change in condition.
POCO replaced over head neutral due to tree rat damage and it appeared to resolve problem for a breif period. (Maybe it was just an illusion). Since return of problem, they have checked twice and declared power to both leg fine.
What isn't being looked at? What should be tested next? What are the code words that POCO responds to? Thanks.