You have two (2) things going on here. You have fire and/or smoke doors which need to release on fire alarm. These doors are also part of an access control system and that needs to be disabled on fire alarm. I assume you have an intelligent panel and you can put addressable relays in the field.
You will have one relay that interrupts power to the door holders (normally closed).
You will have a second relay that interrupts power to the security mag locks (normally closed).
When the fire alarm system is activated both relays will open, closing the fire/smoke doors and disabling the security locks.
Normally you won't provide power from the FACP because door holders/locks are power hogs, relatively speaking. You can provide almost any type you want, 24 vac/vdc, 120 ac etc as all relays from any manufacturer will be rated for either, and while the power draw is high relative to the battery capacity of the FACP, it's well below the max for said relays.