It seems to be a tradition that power entry is on top when you come into an enclosure, be it panel or machine. Is there a rule or is it just force of habit?
Grant I do not know what you meanOriginally posted by grant:
So while we know the breakers are generally not required to have line-load identification there are requirements as to the use of the line and load terminals.
How would it be possible to wire a circuit breaker in a way that the "terminals supplying the load" would still be live with the breaker open?380-6(c) Connection of Switches. Single-throw knife switches and switches with butt contacts shall be connected so that the blades are de-energized when the switch is in the open position. Single-throw knife switches, molded-case switches, switches with butt contacts, and circuit breakers used as switches shall be connected so that the terminals supplying the load are de-energized when the switch is in the open position.