power-limited v nonpower-limited

Status
Not open for further replies.

buck

Member
Location
California
Very confused-- can someone tell me the differences between power-limited and nonpower-limited circuits for fire alarm panels.
Question posed to me was---"can I install 120v power in the same conduit,enclosures,etc as fire alarm wiring?" Thanks in advance
 

ron

Senior Member
Re: power-limited v nonpower-limited

Most fire alarm system power supplies are listed as power limited, but some are not. Check the power supply (says it on the supply itself) and manufacturers wiring requirements.
 