power-limited v nonpower-limited

Status
Not open for further replies.

buck

Member
Location
California
Very confused-- can someone tell me the differences between power-limited and nonpower-limited circuits for fire alarm panels.
Question posed to me was---"can I install 120v power in the same conduit,enclosures,etc as fire alarm wiring?" Thanks in advance
 

ron

Senior Member
Re: power-limited v nonpower-limited

Most fire alarm system power supplies are listed as power limited, but some are not. Check the power supply (says it on the supply itself) and manufacturers wiring requirements.
 
Status
Not open for further replies.
Top