I was asked to determine if there is sufficient capacity to add a 200 amp 3 phase load to an existing 1200 amp 3 phase 480 volt MDP.
I hooked up a fluke power logger to the MDP to record the power for 30 days.
I am cretin that I connected the voltage and amperage leads correctly.
however the reading I was getting seems odd.
A and C phase were only pulling about 6 to 8 amps. however B phase was pulling over 160 amps. this MDP powers multiple transformers that step power down to 120/208 volt lighting and appliance panels.
I am not surprised the 3 phases are not balanced, however I do not understand how just one phase could be so much higher than the others... everything in the MDP is 3 phase. I did not note and heavy single pole appliances in the 208 V panels.
Just want to make sure a reading like this is possible and I did not goof something up when connecting the leads of the power logger.
I hooked up a fluke power logger to the MDP to record the power for 30 days.
I am cretin that I connected the voltage and amperage leads correctly.
however the reading I was getting seems odd.
A and C phase were only pulling about 6 to 8 amps. however B phase was pulling over 160 amps. this MDP powers multiple transformers that step power down to 120/208 volt lighting and appliance panels.
I am not surprised the 3 phases are not balanced, however I do not understand how just one phase could be so much higher than the others... everything in the MDP is 3 phase. I did not note and heavy single pole appliances in the 208 V panels.
Just want to make sure a reading like this is possible and I did not goof something up when connecting the leads of the power logger.