Well, the TED engineer told me they'd started out with monitoring the panel main and attempting to profile major loads; they found it unreliable so they created their Spyder to sense individual branches.
Here's an update on the feed upgrade project. On the 11th, a platoon of the EC's workers, and a similar number of Potelco's, the PSE contractor, troops, and PSE Metering, descended on the property. I alas, was on this coast. But I was told/saw imagery that jointly, they:
- With a truck crane, put in the pad for the new 100 KVA xfmr.
- Pulled the 550 ft primary run from the neighbor's xfmr
- Pulled the new 85 ft parallel 350MCM secondary runs to the house.
- Swung the new xfmr over to the pad.
- Terminated the new runs into the xfmr & new main disconnect.
- Removed the old 350MCM to the CT can.
- Removed the old 200A interior CT's and mounting base.
- Used the old CT can as a jbox for the 3 sets of runs to 200A panelboards. (The new 4th panelboard is 150 ft away; it gets a fused disconnect outdoors next to the main. I wanted it inside as well but lost that battle.)
- Pulled the new 300 ft 350MCM from the 37.5 KVA existing xfmr to the outbuilding and terminated it at the meter there.
- At the neighbor's, dug out access to the pad, and snaked the HV cable up into the (live) 25 KVA xfmr.
- Terminated the cable ends, and when everything was connected, hot-stick connected our new feed to the 2nd bushing on that xfmr.
- Phew.
Along the way, PSE Metering pulled one old CT meter, installed a new one for the 600A CT's, and installed a new 320 series direct meter on the barn.
The good news was it had stopped raining a few days before and abstained all day. As Charlie can no doubt relate, this was a welcome break from the month before when the animals were seen lining up 2 by 2.
I was intrigued by several things I (didn't) see. The GC confirmed there was no ground rod driven in under the pad. There's a bundle of bare ground wire emerging from the side of the pad; can't see where it eventually went. I recall PG&E required a driven rod under the pad, and a second one several feet away.
I was also surprised they didn't disconnect the feed to the 25KVA before step 10/11, but nope.