Power Outage During Storm

Status
Not open for further replies.

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
What exactly happens during a lightning storm that causes the power to go out but usually comes back on in a few seconds to a minute?
 
Spark arresters (sp?) are on the power poles. Reclosers are at the substation.


From Eaton https://www.eaton.com/content/dam/e...ecloser-definition-information-td280027en.pdf

Reclosers are used throughout the power distribution system,from the substation to residential utility poles. They range fromsmall reclosers (Figure 1) for use on singlephase power lines, tolarger three-phase reclosers (Figure 2) used in substations and onhigh-voltage power lines up to 38,000 volts
 
Reclosers are used throughout the power distribution system,from the substation to residential utility poles. They range fromsmall reclosers (Figure 1) for use on singlephase power lines, tolarger three-phase reclosers (Figure 2) used in substations and onhigh-voltage power lines up to 38,000 volts

Interesting. It's the latter that I am aware of. My boss set one off one evening due to a misadventure at the municipal water treatment plant.
 
At a substation?
They are at substations as well as various points throughout the distribution system.

By placing them throughout the system, when a fault occurs that doesn't get cleared happens it isolates a section of the circuit rather than the entire circuit being down. Substations out here usually have one recloser per circuit leaving the substation. In rural areas the main trunk of the circuit may not have many reclosers on it, but will have one near the tap to each major branch off that main trunk.

If you only had one at the source, every time something happens the entire circuit would be down and there would be that much more line to have to investigate to find the problem.
 