Hi,
With reference to this thread -
http://forums.mikeholt.com/showthread.php?t=79044&page=2
Part of the answer states:
(6) For a single phase, 2-pole, 208V load, assign half that kva to each of the two phases to which the load is connected.
Could anyone explain the theory/maths behind this statement please.
I am currently working on a 2-pole trace heating system and am trying to work out this exact question...
Why, in a two pole system, do you get (when measured) half the current in each phase conductor to the single resistive load? Or in reference to your answer - Why split the wattage evenly? What is the theory behind this?
Welcome to the forum, Matt. :thumbsup:
FWIW, your link went to the wrong thread (for me). Here's a link to the post you quoted...
http://forums.mikeholt.com/showthread.php?t=54480&p=395522#post395522
The statement quoted is in reference to line current calculations on a 3? system, where the individual load currents are combined. Let's use 10A 1? loads as an example. The current through the two wires going to an individual load is 10A.
Now let's say you have 3 connected AB, BC, and CA. There will be two connected to leg A (AB and CA). Because the currents are out of phase, their currents combined is 17.32A. Assuming a 208/120V system...
10A ? 208V ? 3 = 6240VA
6240VA ? (208 ? 1.732) = 17.32A per leg
Where the system is 208/120, you multiply 17.32A times 120V and you get 2078.4VA. Each load by itself is 10A times 208V for 2080VA. The difference is rounding error. But you can see the VA on one leg is the same as one load... or half of each of the two connected loads (1/2 times 2 is 1). The reason the VA is halved is because not all load calculations have exactly balanced loads. What if you had three loads at 10, 15, and 20A. While summing half the VA of each connected load per leg is not completely accurate, it is a conventionally-accepted method.