Is PPE required to plug in 60amp or 100amp ,welder ,power plugs ???
If plugging in hot, you would have a possible arc flash hazard and would be required to wear proper PPE (as determined by the arc flash study) and be trained on the hazards.
I have never heard of such a thing, can you provide a reference?
Says nothing about de-energizing the receptacle.110.9(B)(4) Connecting Attachment Plugs
(a) Employees' hands shall not be wet when plugging and unplugging flexible cords and cord-and-plug-connected equipment if energized equipment is involved.
(b) Energized plug and receptacle connections shall be handled only with insulating protective equipment if the condition of the connection could provide a conductive path to the employee's hand (if, for example, a cord connector is wet from being immersed in water).
I would read from the use of the term "emergency" in there that they are designed to suffer this level of misuse just once, and then be replaced, unless they have a number in the spec sheet contradicting that.Plugs may be withdrawn in an emergency under full rated loads without separate disconnect switches" So they are designed to break under load in an emergency only.