A electrical testing company came in and did a power analysis and did not provide a engineers report of recommendations. We were asked to look into the problems they were having.
The customer is a hospital and of course can not shut off power to check or do testing, which creates its own set of problems.
There is excessive noise on all phases as well as harmonics. The facility is 20+ yrs old. Dealing with a 480V primary 120/208V 50KVA Westinghouse transformer with a name plate temp. rise of 5 degrees C. feeding 7 panels on 3 floors with the neutral bars being used as feed thru end to end. Load is operating at 1/3 of nameplate and balanced fairly close.
Transformer is running hot and suspect the harmonics is playing a major factor in the problem.
Grounding of X0 was installed on a water pipe not building steel which I personally don't agree with.
I seem to have more questions than answers. While increasing the KVA rating will help the heat issue, not 100% sure that would be the right way to go since more equipment is becoming electronic in the medical field.
Thinking of maybe a K rated xfmr but not sure cause of the small motor loads be served as well.
The customer is a hospital and of course can not shut off power to check or do testing, which creates its own set of problems.
There is excessive noise on all phases as well as harmonics. The facility is 20+ yrs old. Dealing with a 480V primary 120/208V 50KVA Westinghouse transformer with a name plate temp. rise of 5 degrees C. feeding 7 panels on 3 floors with the neutral bars being used as feed thru end to end. Load is operating at 1/3 of nameplate and balanced fairly close.
Transformer is running hot and suspect the harmonics is playing a major factor in the problem.
Grounding of X0 was installed on a water pipe not building steel which I personally don't agree with.
I seem to have more questions than answers. While increasing the KVA rating will help the heat issue, not 100% sure that would be the right way to go since more equipment is becoming electronic in the medical field.
Thinking of maybe a K rated xfmr but not sure cause of the small motor loads be served as well.