For residential use it is a total swindle.
For commercial use if POCO charges a low PF penalty it might actually eventually pay for itself. But it will over or under correct depending on what loads are turned on at any given time.
The residential simulation used an unloaded motor, so the PF was at its absolute worst. Sure it cut the amps from POCO in half, but that would not have changed the
watts as measured with a POCO watt hour meter or a Kill-A-Watt (TM) plug in meter one bit. (Well, it actually could increase them very slightly under some circumstances.)
The actual residence installation with the measured PF of .05 is an anomaly, with the meter probably wired incorrectly, or maybe the only load being a
very efficient transformer with no load at all on the secondary.
Exactly as stated by everyone from the start: for a residence, it will not save any money at all and is a total rip off.
(PS: did you notice in the demo that the neutral lead was landed on the "ground bar". If that was not actually the service panel with ground and neutral bonded, you have a very much non-code installation! And probably unsafe too.)