Eclectic engineer
Member
- Location
- USA
- Occupation
- Engineer
A 3-phase 100A 120/208V panel contains 6 x 40A EV charging circuits connected to it. These EV chargers are 1-phase loads that operate at 208V. While the circuit breakers are rated for 40A, the max. amp draw is restricted to 32A because of the continuous load rule.
The 6 chargers are controlled by a software that restricts the total amperage draw from the panel to 80A. Each charging circuit uses a double-pole breaker that uses 2 out of the 3 phases of the panel. Following is the configuration -
Charger 1 - L1/L2
Charger 2 - L1/L2
Charger 3 - L2/L3
Charger 4 - L2/L3
Charger 5 - L1/L3
Charger 6 - L1/L3
My question -
When all 6 chargers are actively charging EV's, how will the amps be distributed across the 3 phases? Since the load limit is set to 80A, I am thinking that each charger will get 80/6 = 13.33A each. Is this right?
If it is 13.33A, then each phase is only loaded to 13.33 x 4 = 53.32A based on the connection combo. listed above.
I am a bit confused here. While each phase can go up to 80A, the calculation only adds up to 53.32A.
How can I ensure that each phase also totals up to 80A?
The 6 chargers are controlled by a software that restricts the total amperage draw from the panel to 80A. Each charging circuit uses a double-pole breaker that uses 2 out of the 3 phases of the panel. Following is the configuration -
Charger 1 - L1/L2
Charger 2 - L1/L2
Charger 3 - L2/L3
Charger 4 - L2/L3
Charger 5 - L1/L3
Charger 6 - L1/L3
My question -
When all 6 chargers are actively charging EV's, how will the amps be distributed across the 3 phases? Since the load limit is set to 80A, I am thinking that each charger will get 80/6 = 13.33A each. Is this right?
If it is 13.33A, then each phase is only loaded to 13.33 x 4 = 53.32A based on the connection combo. listed above.
I am a bit confused here. While each phase can go up to 80A, the calculation only adds up to 53.32A.
How can I ensure that each phase also totals up to 80A?