Power Socket Adapter w/breaker

HoosierSparky

Senior Plans Examiner, MEP
Location
Scottsdale AZ
Occupation
Senior Plans Examiner
Would adding a Power Socket Adapter w/breaker to a MSP violate 2020 NEC 230.71(A)? The addition would be adding an additional disconnect to conductors connected to the service feed.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
You're talking about a meter socket adapter, right?

No, that would not be a violation. I think you meant 230.71(B). In any case, it would not be an additional service disconnect in the same enclosure. It would comply with either 230.71(B)(1) or (4).
 

HoosierSparky

Senior Plans Examiner, MEP
Location
Scottsdale AZ
Occupation
Senior Plans Examiner
I believe you are incorrect. The socket adapter sits behind the meter and provides a LINE SIDE TAP prior to the main disconnect. The PV breaker on the socket would violate 230.71(A). This is only for NEW panels under 2020 NEC. I could see allowing it for existing MSP's.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
No, the socket adapter is not in the same compartment. The meter side of a meter main is its own compartment. It definitely meets 230.71(B)(4).

Read the whole thing.
 