Ok I have got opinions from 3 different electricians and each are saying different things. Here is my situation
My utility service meter is outside my building , just 2 feet inside my building the electric is split inside a metal enclosure, were all 4 wires coming into the building are split to 2 each. So now there are 8 wires total. ( I have a delta system 120/120/208 + neutral .)
4 wires run to a mains 200 amp breaker panel right above the metal enclosure were the wires are split, and the other 4 wires go to another large 200A disconnect 1 foot to the right of the metal enclosure . The neutral bond to case is only in the large disconnect, were the water pipe wire is also connected. that large disconnect feeds another sub breaker panel.
There is no neutral bond to case in the mains panel above the metal enclosure .. Is this right? OR should the neutral bond and water pipe be were the neutral is split in the metal enclosure?
My utility service meter is outside my building , just 2 feet inside my building the electric is split inside a metal enclosure, were all 4 wires coming into the building are split to 2 each. So now there are 8 wires total. ( I have a delta system 120/120/208 + neutral .)
4 wires run to a mains 200 amp breaker panel right above the metal enclosure were the wires are split, and the other 4 wires go to another large 200A disconnect 1 foot to the right of the metal enclosure . The neutral bond to case is only in the large disconnect, were the water pipe wire is also connected. that large disconnect feeds another sub breaker panel.