Sorry, a little long of a write-up, but it's a good mystery if you like them:
The boss man sent me to this house to install an in-panel surge suppressor that the homeowner requested.
When I came to the place, this is what the h/o told me:
Apparently, there was a power surge that fried some appliances about a week ago.
It happened on a bright, clear day - no winds, no rain or lightning.
The neighbors did not have any issues (the h/o went around and asked), although one of them said that his whole-house generator kicked in.
Here is the aftermath:
Two surge strips in the house burned up - they both smoked, but the connected TV, cable box and other misc. electronics survived.
The fridge stopped working.
I was thinking, maybe it's a bad neutral, but probably not; The line-to-line loads were affected, too: The 240V A/C compressor blew up. The starting capacitor exploded, and after replacing the capacitor, the a/c guy told the h/o that there is a lot more damage than that.
The homeowner filed a complaint with the POCO, so they said "we don't know" and then came in and installed a power monitor into his meter socket. It's still there.
The service is an underground lateral from a pad transformer on the side of the road stubbing up into a meter on the side of the house.
It's a 200A service.
Just for the heck of it, I put my clamp around phase 1 and 2 - both read roughly around 3A.
The neutral, however, read 2A (shouldn't it have been close to a zero?). Tried again and again, to make sure some other load didn't kick in while I was repositioning the clamp - same result.
The current on the neutral went to zero when I opened the main breaker, which is probably a point against the bad utility neutral theory.
The L1 and L2 to neutral showed 120 volts give or take. The L1 to L2 showed 235 volts (again, strange). My clamp multimeter is a decent Klein model - never had any accuracy issues with it.
Nothing on the surface shows any present issues with the service.
Nothing else strange happened again since the apparent surge (1 week ago) - no lights flickering or any other appliances burning up, even though they had winds and rain since then.
I told the h/o to wait with his surge suppressor until the POCO is done with the monitoring, and asked him to let me know what they say (if they say anything at all, of course - it seems to be against their interest to fess up to something at this point).
At this point this is strictly academic - I am curious more for my own knowledge, since the h/o is duking it out with the POCO.
I did not share any of my own theories with him (not that I have any).
Any other thoughts as to what could have happened on that clear sunny day?
Why is the neutral current 2A higher than the sum of the L1+L2 while the main breaker is on?
The boss man sent me to this house to install an in-panel surge suppressor that the homeowner requested.
When I came to the place, this is what the h/o told me:
Apparently, there was a power surge that fried some appliances about a week ago.
It happened on a bright, clear day - no winds, no rain or lightning.
The neighbors did not have any issues (the h/o went around and asked), although one of them said that his whole-house generator kicked in.
Here is the aftermath:
Two surge strips in the house burned up - they both smoked, but the connected TV, cable box and other misc. electronics survived.
The fridge stopped working.
I was thinking, maybe it's a bad neutral, but probably not; The line-to-line loads were affected, too: The 240V A/C compressor blew up. The starting capacitor exploded, and after replacing the capacitor, the a/c guy told the h/o that there is a lot more damage than that.
The homeowner filed a complaint with the POCO, so they said "we don't know" and then came in and installed a power monitor into his meter socket. It's still there.
The service is an underground lateral from a pad transformer on the side of the road stubbing up into a meter on the side of the house.
It's a 200A service.
Just for the heck of it, I put my clamp around phase 1 and 2 - both read roughly around 3A.
The neutral, however, read 2A (shouldn't it have been close to a zero?). Tried again and again, to make sure some other load didn't kick in while I was repositioning the clamp - same result.
The current on the neutral went to zero when I opened the main breaker, which is probably a point against the bad utility neutral theory.
The L1 and L2 to neutral showed 120 volts give or take. The L1 to L2 showed 235 volts (again, strange). My clamp multimeter is a decent Klein model - never had any accuracy issues with it.
Nothing on the surface shows any present issues with the service.
Nothing else strange happened again since the apparent surge (1 week ago) - no lights flickering or any other appliances burning up, even though they had winds and rain since then.
I told the h/o to wait with his surge suppressor until the POCO is done with the monitoring, and asked him to let me know what they say (if they say anything at all, of course - it seems to be against their interest to fess up to something at this point).
At this point this is strictly academic - I am curious more for my own knowledge, since the h/o is duking it out with the POCO.
I did not share any of my own theories with him (not that I have any).
Any other thoughts as to what could have happened on that clear sunny day?
Why is the neutral current 2A higher than the sum of the L1+L2 while the main breaker is on?