It's been stormy here and power outage have been common. I had a lady call me Friday and say that her mobile home power went out a couple of times, came back on, tripped a breaker and burned out some bulbs. I went out, reset the breaker, turned on everything and read 1-amp. I thought that it was going to be a loose neutral but when I read the voltage on the legs I had 119v and 124v.
Thinking about it now maybe I should have turned on a large appliance then read the voltage. I've seen lost or weak service neutrals before and this didn't look like one to me. Is a 5-volt difference between legs something to be concerned about when there are no heavy loads on? I also read resistance from ground to neutral and got 0Ω in a segregated panel with my t5-600.
The meter is a few doors down. I assume the bonding jumper and grounding rod are there. I couldn't get access.
Yesterday she told me that an Amazon brand power strip plugged into the kitchen counter made a noise and smoked a bit with nothing plugged into it. She threw it out.
She texted me today and said:
"This morning the lights flickered a few times, power went out and came back on but not 100%, flickered again, bulb in bathroom popped. So I called PG&E and the guy came out and checked where the meter is two doors down and said everything looked okay there."
I've been thinking power surge from the storm but this has to be a loose neutral right?
I checked the lugs in her panel and they are tight. PG&E checked the meter but said the portion between the meter and her coach are the responsibility of the park.
The park has a box outside her coach but it's locked. She called the park and they told her that they'll have someone look at it but if it isn't their fault she will be billed for it.
Thanks
Thinking about it now maybe I should have turned on a large appliance then read the voltage. I've seen lost or weak service neutrals before and this didn't look like one to me. Is a 5-volt difference between legs something to be concerned about when there are no heavy loads on? I also read resistance from ground to neutral and got 0Ω in a segregated panel with my t5-600.
The meter is a few doors down. I assume the bonding jumper and grounding rod are there. I couldn't get access.
Yesterday she told me that an Amazon brand power strip plugged into the kitchen counter made a noise and smoked a bit with nothing plugged into it. She threw it out.
She texted me today and said:
"This morning the lights flickered a few times, power went out and came back on but not 100%, flickered again, bulb in bathroom popped. So I called PG&E and the guy came out and checked where the meter is two doors down and said everything looked okay there."
I've been thinking power surge from the storm but this has to be a loose neutral right?
I checked the lugs in her panel and they are tight. PG&E checked the meter but said the portion between the meter and her coach are the responsibility of the park.
The park has a box outside her coach but it's locked. She called the park and they told her that they'll have someone look at it but if it isn't their fault she will be billed for it.
Thanks