Question on electric supplied to a farm. Single phase 120/240 power comes overhead from the power company transformer to a pole in the farm yard down to the meter and back up the pole where it goes overhead to several farm buildings and the house. There is a disconnect on the pole that would shut off all power to all buildings including the house. There is no overcurrent protection on the pole. There is only one breaker panel in the house. Question 1) Does the disconnect on the pole make the house breaker panel a subpanel where the neutral and equipment ground bus bars have to be isolated? I say no but the guy building the house says yes. Question 2) Why do you need 4 wire from the pole to the main breaker in the house? If the power came directly to a meter on the house from the transformer it would just be 3 wire, 2 hots and a neutral. I am just doing the inside wiring so only question 1 affects me as far as whether to bond the neutral and equipment ground at the breaker panel.