If the individual breaker is the "disconnect" then the breaker must be rated at 60A or more.(D) All Others For all other installations, the feeder or branch-circuit disconnecting means shall have a rating of not less than 60 amperes.
Originally posted by don_resqcapt19:
Mike,
Just to stir the pot a bit.
If the individual breaker is the "disconnect" then the breaker must be rated at 60A or more.(D) All Others For all other installations, the feeder or branch-circuit disconnecting means shall have a rating of not less than 60 amperes.
Don
If the FEEDER is protected at the point of origin then the FEEDER disconnect is in compliance.225.39 Rating of Disconnect.
The feeder or branch-circuit disconnecting means shall have a rating of not less than the load to be supplied,
In the house, and probably in the main panel, there will be a breaker that protects the feeder conductors leading to the garage. That is the "feeder disconnect" to which you refer. But I think 225.39 is saying that it is the disconnect (or set of up to 6 disconnects) located at the garage, and not the one inside the house, that must have a rating of 60 amps or more. Throughout 225, it is talking about the disconnect(s) that serve(s) the garage, and it means the one(s) just outside the garage or inside the garage. So Don's stirring of the pot was to inquire whether each of the six breakers (serving as the disconnects for the garage) must be at least 60 amps.Originally posted by jwelectric: If the FEEDER is protected at the point of origin then the FEEDER disconnect is in compliance.
It states that this disconnecting means is for the feeders or branch circuits. These feeders or branch circuits will be calculated by 220.The feeder or branch-circuit disconnecting means shall have a rating of not less than the load to be supplied, determined in accordance with Parts I and II of Article 220 for branch circuits, Parts III or IV of Article 220 for feeders, or Part V of Article 220 for farm loads. In no case shall the rating be lower than specified in 225.39(A), (B), (C), or (D).
225.39 is not talking about "overcurrent protection." It is talking about "a disconnecting means." I know you are not trying to pass these two off as being interchangeable. But the fact that they are not interchangeable helps support my case.Originally posted by jwelectric: A disconnect for a feeder or branch circuit would go where? Would it be at the place of origin or on the load side of the conductors? Can I protect my receptacles (general purpose circuit) by placing the disconnect (OCPD) at the end of the circuit?
I often have the same problem trying to understand your view.Originally posted by jwelectric:
This is so simple that I have a hard time understanding the confusion of others.
Yes it does, if that duplex does not comply with 225.32.Originally posted by jwelectric:
3) Does the 15 amp circuit outlined in 225.39 (A) require a disconnect at the second building if it only supplies a duplex receptacle
Great idea but not required by the code! When you have a service disconnect, the main switch or breaker does not kill the power to the building either!The idea IMO is to kill the power to the buildings wiring for safety or service.
It kills power to everything except the box in which the disconnect is located, and everything upstream (which should be outside the building). From the perspective of the fire fighter who is about to spray water all over the place (except, perhaps, right into the service disconnect itself), that building is de-energized. I think this is the reason that we can't install more than one service to a single building (except in very limited circumstances).Originally posted by websparky:When you have a service disconnect, the main switch or breaker does not kill the power to the building either!
We both over looked something, a duplex would not meet the requirements of 225.36 or it's exception, so that duplex needs a disconnect which may be a snap switch.Originally posted by iwire:
Yes it does, if that duplex does not comply with 225.32.Originally posted by jwelectric:
3) Does the 15 amp circuit outlined in 225.39 (A) require a disconnect at the second building if it only supplies a duplex receptacle
The idea IMO is to kill the power to the buildings wiring for safety or service.
I agree with almost everything you say here except this:Originally posted by charlie b:
But I also think that the intent is to make sure the "other building" has enough power to handle its loads. So if the MLO panel as a whole is rated at least 60 amps, and if the sum total of the 6 breakers is at least 60 amps (hard to imagine this not happening), then I think it would satisfy 225.39.
230.80 says that where the disconnecting means for a service consists of more than one switch or circuit breaker, the combined ratings of all the switches or circuit breakers must not be less than the ratings in 230.79 (which mirror the requirements in 225.39). There is no parallel requirement for this in article 225. Which, if you think about it, makes perfect sense since we're talking about a feeder here instead of a service. We already have overcurrent protection ahead of the feeder conductors, so there's no need for the combined rating of the breakers serving as disconnecting means to total 60 amperes. Only that the enclosure that these disconnecting means are located in to be rated at least 60 amperes.and if the sum total of the 6 breakers is at least 60 amps (hard to imagine this not happening), then I think it would satisfy 225.39.