S sidecutter New User Aug 3, 2021 #1 Is romex (#10 awg NMWG) allowed to be run from Main Panel (outside), to A/C condenser location about 20 feet away via underneath the mobile home?
Is romex (#10 awg NMWG) allowed to be run from Main Panel (outside), to A/C condenser location about 20 feet away via underneath the mobile home?
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Aug 3, 2021 #2 No.
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Aug 3, 2021 #3 334.12(B)(4) In wet or damp locations.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 3, 2021 #4 See 550.15(H)