I've just re-read this fire pump article in EC&M magazine;( http://ecmweb.com/nec/electric_power_pump/ ) and still somewhat unclear on conductor sizing for the fire pump controller.
The article has an example where they are using the locked-rotor amps to size the conductors for the fire pump controller, is this a mistake. I can't find a reference in the 2005 or 2008 NEC where it states that the locked rotor amps should be used for this calculation. I understand the calculations for the fire pump motor calculation and the overcurrent protection sizing. Shouldn't the (full load amps X 1.25) be used to determine the conductor size for the fire pump controller instead of using the locked-rotor amps?
Has anyone else read this article and had the same question? What am I missing here?
Thanks for any responses.
Ricky--
The article has an example where they are using the locked-rotor amps to size the conductors for the fire pump controller, is this a mistake. I can't find a reference in the 2005 or 2008 NEC where it states that the locked rotor amps should be used for this calculation. I understand the calculations for the fire pump motor calculation and the overcurrent protection sizing. Shouldn't the (full load amps X 1.25) be used to determine the conductor size for the fire pump controller instead of using the locked-rotor amps?
Has anyone else read this article and had the same question? What am I missing here?
Thanks for any responses.
Ricky--