Power transformer case bonding

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
We have several 3MVA power XFMRS on site 4160-480V , 3 ph 3 wire solidly grounded- with diagonally opposed NEMA ground pads at the base for case bonding. The inspector said it’s not required to bond the case per NEC but it was common practice to do so. Comments?


Sent from my iPhone using Tapatalk
 

Dale001289

Senior Member
Location
Georgia
We have several 3MVA power XFMRS on site 4160-480V , 3 ph 3 wire solidly grounded- with diagonally opposed NEMA ground pads at the base for case bonding. The inspector said it’s not required to bond the case per NEC but it was common practice to do so. Comments?


Sent from my iPhone using Tapatalk

I don’t believe the case bonding is required by NEC as long as you ground and bond per 250.30


Sent from my iPhone using Tapatalk
 

ron

Senior Member
If the XFMRs are solidly grounded, then there is likely a bond between the X0 and the transformer case / core in some fashion. The grounding electrode conductor also connects to the case. The ground pads may be supplementary for additional grounding and not required if the case is bonded in some other fashion.
 

david

Senior Member
Location
Pennsylvania
We have several 3MVA power XFMRS on site 4160-480V , 3 ph 3 wire solidly grounded- with diagonally opposed NEMA ground pads at the base for case bonding. The inspector said it’s not required to bond the case per NEC but it was common practice to do so. Comments?

Sent from my iPhone using Tapatalk
250.30 (A)(2) supply side bonding jumper
From the source enclosure to the first disconnect enclosure.
If the bonding jumper is a wire type it would connect to that pad
the
The system bonding jumper will eather be at the source or the first disconnect.
I don't know what was ment by its ok to do so.

It's required eather at the source or first disconnect but not at both locations

Exterior transformers you could see it at both locations if earth is the ony other connection between them
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
The case is required to be bonded and grounded. It may come bonded from the factory.

I gather that the 'not required but common practice' part refers specifically to the diagonally opposite grounding pads. See:

 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
The case is required to be bonded and grounded. It may come bonded from the factory.

I gather that the 'not required but common practice' part refers specifically to the diagonally opposite grounding pads. See:


Yea sir - that’s a good thread
Thanks


Sent from my iPhone using Tapatalk
 

bobby ocampo

Senior Member
We have several 3MVA power XFMRS on site 4160-480V , 3 ph 3 wire solidly grounded- with diagonally opposed NEMA ground pads at tWhe base for case bonding. The inspector said it’s not required to bond the case per NEC but it was common practice to do so. Comments?