if the requirements for the power transformer are the following:
cooling: ONAN
continuous power rating with 55 deg.rise over 40 deg. ambient= 15MVA
Overload Power Ratings: Transformers shall be capable to supply the following load cycle within the specified temperature rise at 40°C ambient temperature:
1) 100% of continuous rating indefinitely 55 degrees C rise
2) Followed by 150% of continuous rating for two hours 65 degrees C rise
3) Followed by 300% of continuous rating for five minutes 75 degrees C rise
How would be transformer's power rating indicated as ?
Is it 55/65/75 which correspond to 15/25/45MVA ? Am I correct. Thanks