Re: power wiring practice of variable frequency drives
Provided the wire meets NEC 430.22(A). This may be more of an issue on the drive input side as it is 125% of drive rating, not motor nameplate. I would strongly suggest reviewing the recommended grounding instructions and following them. Although special cables are not required, depending on distance between the motor and drive may be worth using. The last feedback I got from a VFD OEM was their recommendation is to use conductors wrapped in foil and terminate the foil at the motor ground and VFD ground to help reduce/eliminate high speed switching frequency carrying into the motor.