It's one of those things that make me go aghhagahagaga. You'll see a long series loop of similar devices, Omron ice cube devices in a safety circuit, looping through everyone's equipment. Somewhere in the circuit there's a small control contactor coil load that is blowing out the contacts in the ice cube device, 50 ft away in someone else's control cabinet.
But it's intermittent and may latch on the next power cycle. Otherwise it could be anywhere, or on someone's very expensive safety circuit board. It can be difficult to find, but when you do one look will tell you, someone should have suppressed the inductive kick off the control contactor coil load.
If there's only one, socket mounted, and you know where it is, you're golden.