We have a powerflex 70 VFD driving a pump for a mobile LNG Refueler.
It's wired into 480 shore power and nearby loads are causing some low voltage faults to stop the VFD from operating.. I've changed parameters 174, and 175 to allow auto restart if the faults clear within 30 seconds. The issue is that if the VFD is power cycled these two settings revert back to default and we're left with the same problem.
I've tried using HIM copycat to save all settings to the memory as well as saving the active user set with the new settings, but still don't seem to be having much luck.
Am I missing a step?
It's wired into 480 shore power and nearby loads are causing some low voltage faults to stop the VFD from operating.. I've changed parameters 174, and 175 to allow auto restart if the faults clear within 30 seconds. The issue is that if the VFD is power cycled these two settings revert back to default and we're left with the same problem.