spark-e-eng
Member
- Location
- hemlock, MI
I have recently replaced a AB 1336 VFD with an AB Powerflex 753 drive and now have the drive faulting on motor overload (Fault code 7). Prior to replacing the drive, they had no operational issues. Everything has been checked mechanically for any issues that could be causing the overload and none were found. According to the manual the overloads are set based on the nameplate FLA and service factor (1.00 SF, 60HP 71.2A for inverter duty, 75HP 87A for Sine wave duty). I know that the NEC has a provision for increasing the motor overloads to 130% in certain applications for 1.00 service factor motors, but how do we set that in the drive since we are just giving the drive the FLA? I watched the amp output on the drive and it gets up to about 87A at about 45Hz and keeps backing off until it eventually faults on OL. I spoke with drive technical support and they were not very supportive.
Any ideas on how to increase the overload setting to 130% to maintain compliance with NEC, yet allowing us to run? I should also mention that this drive is on a mixer and is located about 150-200ft from the motor.
Any ideas on how to increase the overload setting to 130% to maintain compliance with NEC, yet allowing us to run? I should also mention that this drive is on a mixer and is located about 150-200ft from the motor.