Been wondering just what was going on with a system. Unfortunately, it's one of those situations where there are too many fingers in the pot, so I've stepped back until called again.
This is a water transfer system with a small priming pump feeding a large pressure pump. Both are centrifugal, and both are on VFDs. The priming pump is a powerflex. There is no pressure indication between the pumps. The priming pump always has at least 5 ft of suction head. How the speed command is determined, I don't know, not sure it matters for my question.
Got called out because the priming pump was tripping on overcurrent. FLC = 38A. Changed parameter A179 to 30A and A182 to 1 (Clim). Tried to operate system and got a Stall Fault. Seemed really odd, since it's a centrifugal pump. How could it stall? Anyhoo, Changed parameter to 37A and it worked ok and left. Later, I heard that on occasion it would still trip out on Stall Fault, but what I did seemed to improve things. In the meantime, someone else got into the program, so who knows what's going on there...
Soooo, It's likely that I will get involved again. Hoping some of you fine folks can educate me on what might be going on. Could it be that the VFD drive sensed a great deal of slippage when reducing the hz to limit the current and called it a stall? Maybe a mechanical issue?
This is a water transfer system with a small priming pump feeding a large pressure pump. Both are centrifugal, and both are on VFDs. The priming pump is a powerflex. There is no pressure indication between the pumps. The priming pump always has at least 5 ft of suction head. How the speed command is determined, I don't know, not sure it matters for my question.
Got called out because the priming pump was tripping on overcurrent. FLC = 38A. Changed parameter A179 to 30A and A182 to 1 (Clim). Tried to operate system and got a Stall Fault. Seemed really odd, since it's a centrifugal pump. How could it stall? Anyhoo, Changed parameter to 37A and it worked ok and left. Later, I heard that on occasion it would still trip out on Stall Fault, but what I did seemed to improve things. In the meantime, someone else got into the program, so who knows what's going on there...
Soooo, It's likely that I will get involved again. Hoping some of you fine folks can educate me on what might be going on. Could it be that the VFD drive sensed a great deal of slippage when reducing the hz to limit the current and called it a stall? Maybe a mechanical issue?