And mine is connected with portable cord. That seems to be big in CA, maybe for the disconnect?We have to sleeve it in flex below 8' over here.
And mine is connected with portable cord. That seems to be big in CA, maybe for the disconnect?
The receptacle is a combo single receptacle and screw-in fuse holder.
Needs a disconnect. Maybe there just not in the picture. Yep, that's how it's done. Nothing in the NEC about conduit needed at a certain height.
There may be nothing about conduit needed at a certain height, but there is something in the NEC about protection from mechanical damage being needed below a certain height
Not for this application.
How so?
I will add that NM cable is typically permitted to be run exposed in normally dry locations of dwelling units.There is nothing specifically about height and damage in the NEC that applies to this installation.
I will add that NM cable is typically permitted to be run exposed in normally dry locations of dwelling units.
for my own future reference, what would be an acceptable way to secure/fasten the NM?
I agree there's no exact height given, but one can be inferred. 334.15 talks about exposed NM and it either has to (A) follow the surface of the building or be mounted on a running board, which the wire to a heater is not, or (B) it shall be protected from physical damage where necessary or (C) it shall be protected according to 300.4 or it's up in the framing or it's in protection down the walls. (C) is where we can infer the height (below and out of the framing which offers protection from damage). That leaves (B) which requires protection from physical damage, which surface mounting on the heater unit or ty-rapped to the gas pipe feeding the heater doesn't really offer. Sure, the line is fuzzy. If the wiring stops at five feet (like for a water heater or feeding into the top of a designated sub panel for the heater) you could consider it to be sufficiently protected, but taking it all the way down to the lower section of a heater, just like mounting a receptacle on a brick column in a basement should require protection.
I disagree with that and luckily for me so do seemingly all inspectors in the New England area.
We run exposed NM like that all the time.
You will often see exposed NM down low supplying water heaters, garbage disposers, even outlets on basement walls. A running board is installed and the NM run down it.
We use staples or NM one hole straps.