I need to disconnect all power at a subpanel with an e-stop switch. I will be installing a shunt-trip breaker upstream of the subpanel. I want to provide power to the momentary N/O e-stop switch (which will activate the shunt-trip if the "mushroom" is pressed) from the load side of the shunt trip breaker.
1. The shunt trip breaker is rated at 40A. The terminals for the shunt-trip are rated for max #12AWG. I do not want to take power from a 15A or 20A breaker in the downstream subpanel because, if that breaker is ever tripped or switched off, the e-stop will not function. So I want to pull power for the e-stop/shunt-trip circuit directly off the load side of the shunt-trip breaker. I have read about doing this in several threads about wiring shunt-trip breakers. What I haven't seen addressed is how to protect the e-stop/shunt-trip wiring. If there is a dead short in the e-stop/shunt-trip circuit, I expect the 40A breaker will trip. And it seems I don't really have to worry about overloading the wiring, as the shunt-trip coil is rated to draw only 0.6A at 120VAC. So do I need to install an in-line fuse for this dedicated e-stop/shunt-trip circuit? Or is that unnecessary? If it makes a difference, all the wiring for the e-stop/shunt-trip circuit will be in EMT conduit.
2. For those who have wired shunt-trip breakers in this manner, how do you tap power off the load side of the shunt-trip breaker? I believe double-lugging the #12 shunt-trip circuit wires to the load-side lugs of the breaker is not permitted unless specifically L&L by the breaker's manufacturer. But Polaris connectors (or wire nuts) on the feeder conductors between the shunt-trip breaker and subpanel seems rather clunky.
1. The shunt trip breaker is rated at 40A. The terminals for the shunt-trip are rated for max #12AWG. I do not want to take power from a 15A or 20A breaker in the downstream subpanel because, if that breaker is ever tripped or switched off, the e-stop will not function. So I want to pull power for the e-stop/shunt-trip circuit directly off the load side of the shunt-trip breaker. I have read about doing this in several threads about wiring shunt-trip breakers. What I haven't seen addressed is how to protect the e-stop/shunt-trip wiring. If there is a dead short in the e-stop/shunt-trip circuit, I expect the 40A breaker will trip. And it seems I don't really have to worry about overloading the wiring, as the shunt-trip coil is rated to draw only 0.6A at 120VAC. So do I need to install an in-line fuse for this dedicated e-stop/shunt-trip circuit? Or is that unnecessary? If it makes a difference, all the wiring for the e-stop/shunt-trip circuit will be in EMT conduit.
2. For those who have wired shunt-trip breakers in this manner, how do you tap power off the load side of the shunt-trip breaker? I believe double-lugging the #12 shunt-trip circuit wires to the load-side lugs of the breaker is not permitted unless specifically L&L by the breaker's manufacturer. But Polaris connectors (or wire nuts) on the feeder conductors between the shunt-trip breaker and subpanel seems rather clunky.