I have a screener equipment with two 3/8 HP motors mounted on the exterior across from each other.
Do I need to have 2 separate disconnects to power 2 different 3/8 HP motors for screener?
Or what would be the best way to power those 2 motors ? Please advise.
Attached is the link to the product.
https://www.kason.com/product/VS-FT-HICAP-SCALP/
 
You have to have a compliant disconnect for both motors. They do not have to have one per motor. Did this thing not come with a control panel?

my guess is if either motor is off you can't run the thing anyway so why not just have a single disconnect.
 
You would also have to read the installation instructions. If those little motors have internal thermal protection, all you need is a switch. If not, you will need a Manual Motor Starter at the very least, separate for each one, so those could also function as the disconnects.
 