I have a screener equipment with two 3/8 HP motors mounted on the exterior across from each other.
Do I need to have 2 separate disconnects to power 2 different 3/8 HP motors for screener?
Or what would be the best way to power those 2 motors ? Please advise.
Attached is the link to the product.
https://www.kason.com/product/VS-FT-HICAP-SCALP/
Do I need to have 2 separate disconnects to power 2 different 3/8 HP motors for screener?
Or what would be the best way to power those 2 motors ? Please advise.
Attached is the link to the product.
https://www.kason.com/product/VS-FT-HICAP-SCALP/