lquadros

Member
I would like to know about any regulations or Code that mentions PPE for 24VDC industrial control circuits. The circuits in question do not exceed 10 amps. I am not able to find any info. in our code books in Canada. May be I am not looking in the right direction. Any input is much appreciated. Thanks
 
lquadros said:
I would like to know about any regulations or Code that mentions PPE for 24VDC industrial control circuits. The circuits in question do not exceed 10 amps. I am not able to find any info. in our code books in Canada. May be I am not looking in the right direction. Any input is much appreciated. Thanks

There are no PPE requirements for <50V that I am aware of, unless it is a high energy system (See NFPA 70E 130.1), and 10A is not a high energy system.
 