rpg
Member
- Location
- Kailua, HI, USA
We have a MV switchgear supplier who wants to incorporate the emergency generator PLC controls within the lineup. They claim that they can put the PLC controls in a separate compartment isolated from any other voltage that's >120 and put individual arc flash stickers on each compartment; therefore eliminating the arc flash PPE requirements for the PLC controls compartments per NFPA 70e Table 130.7(C)(15)(A)(a) which states "Work on control circuits with exposed electrical conductors and circuit parts, 120 volts or below without any other exposed energized equipment over 120 volts including opening of hinged covers to gain access". Is this an accepted procedure and are the reduced PPE claims true?