I am tring to determine the PPE and labeling requirements for an electrical control panel fed from a 20A 120V single phase circuit that is supplied by a 37.5KVA transformer. This is using the new NFPA 70E 2009 code.
As per NFPA 70E (2009) 130.3 an arc flash hazard analysis is not required since the voltage is less then 240V, Supplied by one xfmr, and the xfmr is less than 125KVA.
Since an arc flash analysis is not needed, do you use the 130.7(C)(9) table to find the proper PPE? As per the table, working on live parts would be Hazard risk category 1. The new hazard risk catagory 1 now also requires an Arc-Rated face shield.
The new code (130.3(C)) also requires labeling these panels with either the incident energy level or PPE.
Does this mean that the electrical panel needs to be marked as Hazard risk catagory 1 and that the Flash Protection boundary would be 4FT as per 130.3(A)1? When the door is open, the employee would require a face shield if they were within 4ft of energized conductors?
Please provide some guidance because this seems like overkill.
Thanks
As per NFPA 70E (2009) 130.3 an arc flash hazard analysis is not required since the voltage is less then 240V, Supplied by one xfmr, and the xfmr is less than 125KVA.
Since an arc flash analysis is not needed, do you use the 130.7(C)(9) table to find the proper PPE? As per the table, working on live parts would be Hazard risk category 1. The new hazard risk catagory 1 now also requires an Arc-Rated face shield.
The new code (130.3(C)) also requires labeling these panels with either the incident energy level or PPE.
Does this mean that the electrical panel needs to be marked as Hazard risk catagory 1 and that the Flash Protection boundary would be 4FT as per 130.3(A)1? When the door is open, the employee would require a face shield if they were within 4ft of energized conductors?
Please provide some guidance because this seems like overkill.