PPE Requirements for Working on Energized 250VDC Crane Hot Rails

Poppington93

New User
Location
PPA
Occupation
Electrical Maintenance Engineer
I have a question about NFPA requirements for working on live 250VDC crane hot rails, such as removing collector shoes for weekly maintenance without shutting down the entire bay where other cranes are in operation at.

Our DC system is ungrounded and the specific area is fed from a 1600A breaker, old ABB K 1600 to exact. I see this is within NFPA 70E for Category 2, at least for the fault current of this circuit. I want to make sure I am going in the right direction of what PPE is required for this work, or what additional info I will need to determine the best measures for having employees perform the work safer without shutting down the entire bay since we are a high operation mill.
 
I think you'll need an Incident Energy (IE) calculation for that specific bus.
For the first time NFPA Link is not available or I'd list the table that's applicable for shock protection (I think it's 130.4E (B) for DC). I think they're doing maintenance on the NFPA Link forum.
The IE calc downstream of a 1600-amp breaker will likely be more than the 8 calories that Category 2 PPE is rated for, but it depends on how deep you are in the electrical system.
 